Air Conditioning service needed
Air Conditioning service needed
Hello, this is my first post on here.
We need to get the air conditioning units serviced at the apartment, can anyone recommend a company/engineer?
We need to get the air conditioning units serviced at the apartment, can anyone recommend a company/engineer?
Re: Air Conditioning service needed
There is a company (name escapes me) next to L'Orange restaurant that does all of this.
-
logicbob
- CVO Master

- Posts: 1688
- Joined: Tue Oct 17, 2006 3:26 pm
- Location: Hertfordshire / Vale De Milho
Re: Air Conditioning service needed
Try,
Mr. Jacob
Rua da Liberdade, 70
8400-369 Lagoa, Algarve
Portugal
00351 282 353 320
Mr. Jacob
Rua da Liberdade, 70
8400-369 Lagoa, Algarve
Portugal
00351 282 353 320
-
lizzieh
- CVO Senior

- Posts: 211
- Joined: Tue Jan 18, 2005 12:48 pm
- Location: Hayling Island Hants and Val Fontes De Cima Algarve
Re: Air Conditioning service needed
Carlos who's wife Annete works in Sully's bar is a heating engineer. She is there daily from about noon. liz
Re: Air Conditioning service needed
Thanks all for your suggestions, will get some prices. 
-
laserblazer
- CVO Oracle

- Posts: 6209
- Joined: Sun Apr 30, 2006 11:11 am
- Location: Worcestershire and QdP
Re: Air Conditioning service needed
Thanks laserblazer. Also had this guy recommended by another forum member so I've emailed him for price.
Re: Air Conditioning service needed
my air con units are in need of a service soi would be interested in what the prices are please.
-
Van Muylem
- CVO Regular

- Posts: 36
- Joined: Fri Aug 13, 2004 7:31 pm
- Location: Belgium
- Contact:
Re: Air Conditioning service needed
The one and only
Mr. Jacob
Rua da Liberdade, 70
8400-369 Lagoa, Algarve
Portugal
00351 282 353 320
Best regards
Antoine Van Muylem
Mr. Jacob
Rua da Liberdade, 70
8400-369 Lagoa, Algarve
Portugal
00351 282 353 320
Best regards
Antoine Van Muylem
Re: Air Conditioning service needed
Sorry, I completely forgot about Carlos he is also an airconditioning engineer and can re gas your system should it be necessary , good service v reasonable rates
Re: Air Conditioning service needed
does anybody know the prices of servicing&re-gassing air con units ?
Re: Air Conditioning service needed
Do it yourself, all you need to do is clean the filters and give the unit a hoover, that's all they'll do, just read your user guide, even I can do it. 
Re: Air Conditioning service needed
thankspato i will give that a try when im over on feb 12th.i have one unit that dosent get warm though (i have the units that heat&cool)so i dont know if it is low on gas.
-
laserblazer
- CVO Oracle

- Posts: 6209
- Joined: Sun Apr 30, 2006 11:11 am
- Location: Worcestershire and QdP
Re: Air Conditioning service needed
Not all models warm, even if they have the indicators on the unit and remote. Check the actual model number to see.alf1956 wrote:thankspato i will give that a try when im over on feb 12th.i have one unit that dosent get warm though (i have the units that heat&cool)so i dont know if it is low on gas.
Here's a handy guide on aircon servicing http://www.hvac-for-beginners.com/air-c ... oting.html
Re: Air Conditioning service needed
Hi Pato,
Its not just a matter of cleaning and vacing the filters and evaportor.
1.Remove the Filters
2.Unclip the louvers
3. Unclips the slated fins
4.Vacuum the evaportor coil and machine
5.The evaportor coils to be sprayed with coil cleaner and bacteria remover, this should be sprayed on quite heavy.
6.A acid drain cleaner needs to be applied to the drain pan (250ml) and left for 10 mins and then flushed with clean water.
7.Spary the coil fan with plastic fan cleaner and wipe dry
8. Wash fiters and dry, refit filters and all other fittings.
9.Go to the outdoor compressor, connect up your manifold gauges to check working pressures.
10.Run machine on cooling for 15 mins
11. Your disharge pressure should be between 7-9 bar, this is for R410a refrigerant and you will have to check a comparter chart for different refrigerant.
12. Run the system on heat for 15 mins and the pressure should run on 31-35 bar.
13. if pressures are low refrigerant needs to be weighed in.
This 90% of the serice done
Its not just a matter of cleaning and vacing the filters and evaportor.
1.Remove the Filters
2.Unclip the louvers
3. Unclips the slated fins
4.Vacuum the evaportor coil and machine
5.The evaportor coils to be sprayed with coil cleaner and bacteria remover, this should be sprayed on quite heavy.
6.A acid drain cleaner needs to be applied to the drain pan (250ml) and left for 10 mins and then flushed with clean water.
7.Spary the coil fan with plastic fan cleaner and wipe dry
8. Wash fiters and dry, refit filters and all other fittings.
9.Go to the outdoor compressor, connect up your manifold gauges to check working pressures.
10.Run machine on cooling for 15 mins
11. Your disharge pressure should be between 7-9 bar, this is for R410a refrigerant and you will have to check a comparter chart for different refrigerant.
12. Run the system on heat for 15 mins and the pressure should run on 31-35 bar.
13. if pressures are low refrigerant needs to be weighed in.
This 90% of the serice done